DCS Critical signals segregation

S

Thread Starter

sanand

hi all,

For the critical redundant signals as a general industrial practise it will be configured in different I/O cards in case even one set of I/O card failure the other set of I/O cards retain the signal. Now my question, is there any international standard associated with this requirement?

Please let me know,

with best regards,
sanand
 
S

Steve Linehan

Most plant configurations would depend on the safety assement and the decisions that the engineers would take to satisfy the requirements of the HAZOP and CHAZOP. (Safety Review & Control System Operability Review) Some good sources for data on these would be. Safety Instrumented System standards (e.g., ANSI/ISA 84, IEC 61508 & 61511. You can also google "SIL levels" for some good data. Hope this helps

Steve Linehan.
 