I've been doing some research regarding load tap changers, or on-load tap changers. It seems that different manufacturers make different types of transformers/taps depending on the application.
It's really difficult to say what should be done at your site without understanding more about the type of load tap changer at your site.
To my way of thinking about the problem, if the "grid" voltage the generator terminals are seeing (from the low voltage side of the step-up transformer) is really high versus the amount of excitation being supplied to the generator then a lot of leading reactive current will be flowing in the generator stator windings and it's entirely likely that in an effort to reduce the voltage at the generator terminals the excitation system and/or the operators will reduce the excitation which can lead to a very dangerous situation (loss of excitation, or, worse, loss of synchronism (pole slipping)).
So, if it's possible to reduce the voltage on the low voltage side of the step-up transformer with the load tap changer without having a negative effect on the voltage on the high voltage side of the step-up transformer so that the generator excitation can be increased that would seem to be the thing to do <b>based on the information provided.</b>
But, we don't know what will happen to the voltage on the high side of the step-up transformer--which is important to understand. There may be something happening on the high side of the step-up transformer that we don't know about or understand. I've read about some transformers that can change taps and only affect the voltage on one side of the transformer (high or low), and then I've read about some transformers that, when the taps are changed, there is a difference on both sides of the transformer.
So, there's not enough information for us to be of much help. I think you should be working with the grid operator/regulators to understand why the voltage on the low side of the transformer is so high. And, if this only happens on occasion (it's not a typical operating circumstance), why is it happening and what can be done to correct it?
I wish I could be more help. From the lack of other replies, I would guess that there isn't anyone else with any experience in a situation similar to yours that can comment. And, perhaps that's just because there's too much we don't know.
Please write back to let us know how this progresses.
I've been doing some research regarding load tap changers, or on-load tap changers. It seems that different manufacturers make different types of transformers/taps depending on the application.
It's really difficult to say what should be done at your site without understanding more about the type of load tap changer at your site.
To my way of thinking about the problem, if the "grid" voltage the generator terminals are seeing (from the low voltage side of the step-up transformer) is really high versus the amount of excitation being supplied to the generator then a lot of leading reactive current will be flowing in the generator stator windings and it's entirely likely that in an effort to reduce the voltage at the generator terminals the excitation system and/or the operators will reduce the excitation which can lead to a very dangerous situation (loss of excitation, or, worse, loss of synchronism (pole slipping)).
So, if it's possible to reduce the voltage on the low voltage side of the step-up transformer with the load tap changer without having a negative effect on the voltage on the high voltage side of the step-up transformer so that the generator excitation can be increased that would seem to be the thing to do <b>based on the information provided.</b>
But, we don't know what will happen to the voltage on the high side of the step-up transformer--which is important to understand. There may be something happening on the high side of the step-up transformer that we don't know about or understand. I've read about some transformers that can change taps and only affect the voltage on one side of the transformer (high or low), and then I've read about some transformers that, when the taps are changed, there is a difference on both sides of the transformer.
So, there's not enough information for us to be of much help. I think you should be working with the grid operator/regulators to understand why the voltage on the low side of the transformer is so high. And, if this only happens on occasion (it's not a typical operating circumstance), why is it happening and what can be done to correct it?
I wish I could be more help. From the lack of other replies, I would guess that there isn't anyone else with any experience in a situation similar to yours that can comment. And, perhaps that's just because there's too much we don't know.
Please write back to let us know how this progresses.