Hello, it has been a while.
In normal operation on the other 3 GE 7ea Gas Only Simple Cycle units on-site, the TTRF1 would raise through 1950 deg F on up past 1985 deg F through the transfer to Premix Steady State.
The other morning during a cold start (<20 deg F), one of the units here was unable to reach Premix Steady State after a few attempts even once warmed up. This particular unit was ramping up in the normal fashion, Primary, Lean-Lean Pos, Lean-Lean Neg, and then onto Premix Transfer @ 1950 deg F. The issue we are seeing is that rather than having the TTRF1 temperature continue to raise from 1950 past 1985 deg F, this unit was plateauing around 1950 deg F. This temperature dip caused the unit to indicate "Modeless" for a moment and flash back to Lean-Lean Neg mode, eventually leading to an Extended Lean-Lean condition.
All of the unit instrumentation was reading correctly and well in line with the other 3 units that were started successfully alongside this one. (CTDA, CPD, afpap, afpcs, afpbd, afpep, etc.) Going back and looking at historical data, I can see that since 2023 this unit has barely made it to Premix Steady State with TTRF1 hovering just past 1955 deg F during Transfer during cold weather starts. (Fall of 2023 was the last C.I. with GE)
Once in Premix Steady State, this unit has excellent NOx and CO emissions levels while fired around 2055 with <70 deg F spreads at Base in the Summer and Pre-Selected 84MW in the Fall/Winter.
Any feedback or insight into this condition is appreciated.
Thank You,
Bob Grave
In normal operation on the other 3 GE 7ea Gas Only Simple Cycle units on-site, the TTRF1 would raise through 1950 deg F on up past 1985 deg F through the transfer to Premix Steady State.
The other morning during a cold start (<20 deg F), one of the units here was unable to reach Premix Steady State after a few attempts even once warmed up. This particular unit was ramping up in the normal fashion, Primary, Lean-Lean Pos, Lean-Lean Neg, and then onto Premix Transfer @ 1950 deg F. The issue we are seeing is that rather than having the TTRF1 temperature continue to raise from 1950 past 1985 deg F, this unit was plateauing around 1950 deg F. This temperature dip caused the unit to indicate "Modeless" for a moment and flash back to Lean-Lean Neg mode, eventually leading to an Extended Lean-Lean condition.
All of the unit instrumentation was reading correctly and well in line with the other 3 units that were started successfully alongside this one. (CTDA, CPD, afpap, afpcs, afpbd, afpep, etc.) Going back and looking at historical data, I can see that since 2023 this unit has barely made it to Premix Steady State with TTRF1 hovering just past 1955 deg F during Transfer during cold weather starts. (Fall of 2023 was the last C.I. with GE)
Once in Premix Steady State, this unit has excellent NOx and CO emissions levels while fired around 2055 with <70 deg F spreads at Base in the Summer and Pre-Selected 84MW in the Fall/Winter.
Any feedback or insight into this condition is appreciated.
Thank You,
Bob Grave