We have three gensets operated in parallel; one of them 11 KV, has a neutral earthed through resistance. The other two are 400 v connected to delta transformer 0.4KV delta / 11KV star, this star is earthed direct. The 11 KV of those transformers and the first genset are connected to one bus bar, which is connected also to a zigzag transformer with neutral earthed. when the genset 11KV is the only one on the bus, without connecting the Z transformer and the 400 v genset, the neutral ct equal zero.
In case of connecting either the Z transformer or the 400 v genset to the bus with 11 KV genset the neutral CT equal 27AMP measured on 11kv genset, and 12 AMP measured on Z transformer neutral wire, and 15 AMP measured on 400 volt transformer neutral wire. All currents have 148 HZ. please advise is this problem is harmonics or earthing problem?
In case of connecting either the Z transformer or the 400 v genset to the bus with 11 KV genset the neutral CT equal 27AMP measured on 11kv genset, and 12 AMP measured on Z transformer neutral wire, and 15 AMP measured on 400 volt transformer neutral wire. All currents have 148 HZ. please advise is this problem is harmonics or earthing problem?