electric motor

S

Thread Starter

Sensorless

Guys ! I am not 4m electrical background. I just want to know the reason that "when i gave 3 phase supply to a star connected ac motor from a 1 phase to 3 phase converter, then, the multimeter is showing a voltage difference of about 220V between one of the phases and the motor body, even though the motor body has no current leakage through it".

I have not given any earth to my 1 phase to 3 phase voltage converter, so, can this be the reason?
Waiting 4 a genuine reply...

Thank You.
 
R
First of all the frame of your motor and VFD should be earthed for safety. You need to give us some more information, are you seeing 220 V on just one phase to ground or are they all the same?

Roy
 
Sensorless... Please provide the following:

1) The three line-line voltages.

2) The three line-to-ground voltages.

3) The three line currents.

4) The motor ameplate data.

5) Are you using a "true" RMS reading test Instrument?

Regards, Phil Corso
 