There is a til from ge (til 1420-2r1) which can be applied to the gas turbines frame 5-6-and 9. This til is not valid for the turbines and controls supplied after 2003. The title is Lube oil Logic enhancement.
I have to implement the logic in a markv idos. the turbine is frame6 monoshaft which drives a generator. Pratically there was a gas turbine in which the ELOP was stopping automatically during a shut down where the a.c. was lost and also the speed pickups where lost,, and let's add that even 3 pressure switch where not good calibrated.The consequence was damamged bearings
my solution was to take the signal L14HR and let it in a timer of 30 min and the resulting signal i would put it in the L4qez logic instead of the L14hr. Did somebody implemented already this logic somewhere??
Thanks in Advanced
I have to implement the logic in a markv idos. the turbine is frame6 monoshaft which drives a generator. Pratically there was a gas turbine in which the ELOP was stopping automatically during a shut down where the a.c. was lost and also the speed pickups where lost,, and let's add that even 3 pressure switch where not good calibrated.The consequence was damamged bearings