We have 3 GE Frame 9e machines at our site. I am not an E&I guy but since I am in technical services, so I am concerned about out gas turbine tripping so frequently due to EX2000.
Here is what we get from the alarm,
On 6th Jan:
Machine tripped on EX2000 trip alarm at base load of 133 MW.Following alarms enunciated.
Master1- Generic EX2000 trip, Master protective signal, Master protective /turbine trip, Generator
protection trip,EX2K trip,EX2K diag alarm,CTG1C Generator differential trip. Fault code at MarkV EX200
screen was 28 and at EX2000 local panel was 29.
On 7th Jan:
Machine tripped at 134 MW on EX2000 fault. Following alarms and indications noted & View ST saved.
Indication at DGP: 87B, Fault code at Mark V EX2000 screen: 28, Fault code at EX2000 screen(Local):
29. Alarms at MarkV. EXC1-EV17 Master1- Generic EX2000 trip, EXC1_EV19 Master1-field breaker
feed back, Generator protection trip, EX2K diag alarm, EX2K trip.
Machine tripped on several other occasions and each time the card was resetted. DGP was resetted and even changed. The problem was found by our electrical staff (what they claim) but still the machine tripped.
Now we contacted the OEM and they asked us to start the machine and keep it at a preselect load of 80-87 MW.
Can I get a clue from the members what is happening here and why the exciters protection is activating, although our electrical crew claims that they have checked everything but the problem is a GHOST TriP
Here is what we get from the alarm,
On 6th Jan:
Machine tripped on EX2000 trip alarm at base load of 133 MW.Following alarms enunciated.
Master1- Generic EX2000 trip, Master protective signal, Master protective /turbine trip, Generator
protection trip,EX2K trip,EX2K diag alarm,CTG1C Generator differential trip. Fault code at MarkV EX200
screen was 28 and at EX2000 local panel was 29.
On 7th Jan:
Machine tripped at 134 MW on EX2000 fault. Following alarms and indications noted & View ST saved.
Indication at DGP: 87B, Fault code at Mark V EX2000 screen: 28, Fault code at EX2000 screen(Local):
29. Alarms at MarkV. EXC1-EV17 Master1- Generic EX2000 trip, EXC1_EV19 Master1-field breaker
feed back, Generator protection trip, EX2K diag alarm, EX2K trip.
Machine tripped on several other occasions and each time the card was resetted. DGP was resetted and even changed. The problem was found by our electrical staff (what they claim) but still the machine tripped.
Now we contacted the OEM and they asked us to start the machine and keep it at a preselect load of 80-87 MW.
Can I get a clue from the members what is happening here and why the exciters protection is activating, although our electrical crew claims that they have checked everything but the problem is a GHOST TriP