We have a large >300MW hydro pump-gen unit where during start up, the EX2100 is exhibiting the following as of recent:
1. Start command given- unit reaches 95% speed - 41 exciter breaker closes - EX2100 begins to excite the field.
2. Voltage builds (gen output reaches ~16KV) - loud audible hum/buzz is heard from the SCR power cabinet (not typical) - the 41 breaker immediately trips open.
3. Attempted a re-start, similar event.
4. Final restart but using 'Exciter Auto Start', unit goes online without issue.
4. No fault codes other than De-Excitation trip on OIT screen.
5. Troubleshooting in progress, diagnostic codes are De-Excitation Trip.The codes relates to check SCR or diodes, Hall Effect transducer, or EDEX board.
Has any site experienced similar and willing to share? I have little experience and lots to learn with checking SCRs on this vintage unit.
Thanks,
Denis
1. Start command given- unit reaches 95% speed - 41 exciter breaker closes - EX2100 begins to excite the field.
2. Voltage builds (gen output reaches ~16KV) - loud audible hum/buzz is heard from the SCR power cabinet (not typical) - the 41 breaker immediately trips open.
3. Attempted a re-start, similar event.
4. Final restart but using 'Exciter Auto Start', unit goes online without issue.
4. No fault codes other than De-Excitation trip on OIT screen.
5. Troubleshooting in progress, diagnostic codes are De-Excitation Trip.The codes relates to check SCR or diodes, Hall Effect transducer, or EDEX board.
Has any site experienced similar and willing to share? I have little experience and lots to learn with checking SCRs on this vintage unit.
Thanks,
Denis