Yes it's a Frame 9E TurbineWhat is frame of the unit ( Frame 9E ..,?)
Check equipment, which is the cause of the problem in the normal sequence: starting system power, torque converter, fuel control, and acceleration loop.
Check if the AUTO order has been executed.
L48CR_ALM TURBINE SHAFT FAILURE TO BREAK AWAY
The time delay is finished and the turbine shaft does not breakaway.
Check operation of the lifting/jacking oil pump .... if it is a Frame 9..
James
Starting means fault.
Check the operation of the auxiliaries.
Check the starting means.
Yes. The Unit broke away and successfully engaged on Turning gear operations without any intervention other than selecting the cooldown with the auxiliary pumps on circulation.Any update...