Hello Guys,
I have a question about flame detector uneven counts. In Mk-V Idos, the flame indicates:
Flame 2 = 513
Flame 3 = 739
Flame 7 = 374
Flame 8 = 214
(not a DLN Machine)
If all flame indicates logic-1, we continue running the turbine, but if we loose 3 out of 4 flame detectors, we trip. Can anyone explain what it indicates if the flame count shows very high and what it indicates the flame is low in count as in above mentioned readings? Does it indicate over firing, under firing, quality of the gas burnt into turbine, and what is the impact of that on the turbine? We are using Honeywell flame detectors and are brand new installed after a major overhaul on turbine. Spread 1 = 44 DegC and Spread 2 =35 DegC, FSR= 49 @32MW Base, IGV =86Dga, CTIM= 22DegC, TTXM=560, CPD = 9.39Bars
Best Regards,
Mambo
I have a question about flame detector uneven counts. In Mk-V Idos, the flame indicates:
Flame 2 = 513
Flame 3 = 739
Flame 7 = 374
Flame 8 = 214
(not a DLN Machine)
If all flame indicates logic-1, we continue running the turbine, but if we loose 3 out of 4 flame detectors, we trip. Can anyone explain what it indicates if the flame count shows very high and what it indicates the flame is low in count as in above mentioned readings? Does it indicate over firing, under firing, quality of the gas burnt into turbine, and what is the impact of that on the turbine? We are using Honeywell flame detectors and are brand new installed after a major overhaul on turbine. Spread 1 = 44 DegC and Spread 2 =35 DegC, FSR= 49 @32MW Base, IGV =86Dga, CTIM= 22DegC, TTXM=560, CPD = 9.39Bars