The unit is frame 5 with Mark V control systems.
The unit was running for more than 18 hours with 8MW load after GCV/SRV maintenance and recalibration. this morning we did shutdown for oil leak. And during the start up at the FSNL the speed continue to increase till overspeed trip. at the same time I used the Manual FSR control to bring down the speed and to avoid the over frequency trip.
I can see the speed goes up to 5346 rpm,
We did the SRV & GCV calibration yesterday and the unit was started two times without any problems. today we did the P2 pressure transmitter calibration check only and the problem started. customer is asking to recalibrate the P2 transmitters which I don’t agree on
Looking forward for your assistance
The unit was running for more than 18 hours with 8MW load after GCV/SRV maintenance and recalibration. this morning we did shutdown for oil leak. And during the start up at the FSNL the speed continue to increase till overspeed trip. at the same time I used the Manual FSR control to bring down the speed and to avoid the over frequency trip.