We've a PG9171 gas turbine on-site using the Mark V control system. Now, our Mark V system has been showing a Voter mismatch, <R> FPRG_INT alarm.
After this alarm, we did some checks on-site:
I'm quite new to working with the Mark V system and unsure if my analysis of the fault is correct. I'd really appreciate your help in analyzing this issue. If it's a problem with the servo valve, a direct replacement should fix it. However, if it's a controller issue, which part of the control board needs replacement, and would we need to do a LOAD after replacement?
I hope to get your assistance. Thank you so much!
We've a PG9171 gas turbine on-site using the Mark V control system. Now, our Mark V system has been showing a Voter mismatch, <R> FPRG_INT alarm.
After this alarm, we did some checks on-site:
- Checked 3 FPG2 pressure signals: 18.12 bar, 18.24 bar, 18.35 bar, which are quite balanced.
- (FPRGOUT=18.14bar).
- Looked into 2 LVDT signals: 1.74Vrms, 1.77 Vrms, which are pretty similar.
- Examined SRV feedback FSGR: 45.75%, 45.17%, 45.20%, quite balanced.
- Checked FPRG_INT: 58.66%, 38.43%, 37.17%.
- Servo currents FAGR for controllers R, S, T: -42.20%, 15.76%, 20.33%, not balanced.
- No other diagnostic alarms found on L3GSSRV1 module.
I'm quite new to working with the Mark V system and unsure if my analysis of the fault is correct. I'd really appreciate your help in analyzing this issue. If it's a problem with the servo valve, a direct replacement should fix it. However, if it's a controller issue, which part of the control board needs replacement, and would we need to do a LOAD after replacement?