Good day attached is a photo. Anyone know how to clear this system fault
Attachments
-
52.7 KB Views: 10
Good dayGood day attached is a photo. Anyone know how to clear this system fault
Thanks for the quick feedback non the ENIU is part of a remote I/o for a scada system for some power station. They had a short circuit on a power mcb , three i/o's where damaged including part of the backpane. The backpane and the three i/o modules where replaced when the reote i/o was powered the ENIU was showing ok on LED but with sys fault but the rest of the modules are. So we have no indications from the remote i/o on scadaGood day
Any diagnostic alarms or other error code/message associated to this syst fault...
Thanks for clarifying !Thanks for the quick feedback non the ENIU is part of a remote I/o for a scada system for some power station. They had a short circuit on a power mcb , three i/o's where damaged including part of the backpane. The backpane and the three i/o modules where replaced when the reote i/o was powered the ENIU was showing ok on LED but with sys fault but the rest of the modules are. So we have no indications from the remote i/o on scada
Oh thanks alot for the valuable contributionAccording to OEM manual this kind of LED status is indicate the power supply has failed and is no longer supplying sufficient voltage to the backplane...
Always glad to support you !
James
You may have solution to clear the fault & so on the Sys fault led , but the thing is that you must troubleshoot backplane power supply prior ...I will get back to you on the results am communicating with a team on site the station is 900km from where i am
HiGood day All
Thanking you the for the inputs. Had to troubleshoot with site team via whatsapp. Turns out the power supply was okay but after replacing the IO modules that where burnt they put an AI card with the wrong part number. After replacing with the right AI card the error disappeared
Thread starter | Similar threads | Forum | Replies | Date |
---|---|---|---|---|
M | Recurrent Faults in PAC RX3i | Programmable Logic Controller - PLC | 6 | |
A | Modbus TCP/IP communication Modicon M340 to GE PAC RX3i | Modbus | 3 | |
B | Eurotherm PAC T2550 Errors | General Software Chat | 0 | |
B | Eurotherm PAC and Wonderware | General Software Chat | 2 | |
S | Docs for old motorized GE Volt Pac | General Automation Chat | 1 |
by Seth Price
by Munir Ahmad