Generator Frequency

S

Thread Starter

surameen

The 4 pole generator gives frequency 2566. 67HZ. I don't understand how to connect this type of generator in 50HZ system.

pls comment
thank you
 
B

blackstoneboy

what kind of generator is that?? If it is the generator,, it cant have a frequency of that kind. Maybe it is the speed..
 
C
If the system frequency is 50 Hz., then the speed for a 4 pole generator should be 1500 rpm. It seems the frequency of your generator is 1566.67 rpm(and not 2566.67rpm -- please check the input to the display unit) corresponding to the electrical frequency of 52.2235 Hz. This generator can be definitely synchronized with the system of 50 Hz. by reducing the speed of the generator. A normal synchronization is possible.

Hope this clarifies.
 