Gents,
We have a GE gas turbine generator with following specs:
Model: 217210 - 20MVA, 6.6kV, 50Hz, 4 pole, 1500rpm, 0.85 PF, 1750A. Field Amps at rated load is 800A.
We want to tweak the settings of the excitor limiters as follows:
Why we want to change them?
Because the excitor was giving over excitation alarms every time a few large motors were being started at site. So we consulted excitation system provider i.e. Basler Electric, and they suggested the change.
Next step was to consult OEM, GE.
We contacted GE, but they asked us for 'money' to carry out 'dynamic simulation' after which they tell us if these settings, proposed by Excitation system provider, are correct or not.
Honestly speaking, the management does not want to spend money and they seem contended on Basler Electric's settings.
Since the excitation current directly impacts rotor, it is clear that the Limiters are based on Generator Capability Curve. The field amp at rated load is 800A (which is low level setting of excitor limiter and the same current, 800A for 1 sec, is Medium level of excitor setting as well). The high level excitor setting is kept at 1560A for 8sec.(I have no idea for the basis, but it was kept by GE).
With new settings, we will be increasing the low level limit from 800A to 810A and Medium from 800A for 1 sec to 1400A for 20secs and finally high level limiter from 1560A to 1800A for 5 secs.
My question is regarding the Medium and High settings. How can we ensure that these settings don't harm the rotor? I mean rotor is rated for 800A but Medium level will now be 1400A for 20secs, so if the field current rises from the low level excitor setting, the rotor will be exposed to much more current. Motor start ups usually last 15 to 17 secs.
What things we should look at if we don't want to have a dynamic simulation conducted? Excitation system manufacturer is confident these settings which he is proposing are correct.
Has anyone done anything similar at any site? What were the basis? and what were the checks done before the change?
Sincerely,
MRasool
We have a GE gas turbine generator with following specs:
Model: 217210 - 20MVA, 6.6kV, 50Hz, 4 pole, 1500rpm, 0.85 PF, 1750A. Field Amps at rated load is 800A.
We want to tweak the settings of the excitor limiters as follows:
| Excitation Limiters | Existing/Original Settings | Proposed Settings |
| High Level | 1560A | 1800A |
| High Time | 8sec | 5sec |
| Medium Level | 800A | 1400A |
| Medium Time | 1sec | 20sec |
| Low Level | 800A | 810A |
Why we want to change them?
Because the excitor was giving over excitation alarms every time a few large motors were being started at site. So we consulted excitation system provider i.e. Basler Electric, and they suggested the change.
Next step was to consult OEM, GE.
We contacted GE, but they asked us for 'money' to carry out 'dynamic simulation' after which they tell us if these settings, proposed by Excitation system provider, are correct or not.
Honestly speaking, the management does not want to spend money and they seem contended on Basler Electric's settings.
Since the excitation current directly impacts rotor, it is clear that the Limiters are based on Generator Capability Curve. The field amp at rated load is 800A (which is low level setting of excitor limiter and the same current, 800A for 1 sec, is Medium level of excitor setting as well). The high level excitor setting is kept at 1560A for 8sec.(I have no idea for the basis, but it was kept by GE).
With new settings, we will be increasing the low level limit from 800A to 810A and Medium from 800A for 1 sec to 1400A for 20secs and finally high level limiter from 1560A to 1800A for 5 secs.
My question is regarding the Medium and High settings. How can we ensure that these settings don't harm the rotor? I mean rotor is rated for 800A but Medium level will now be 1400A for 20secs, so if the field current rises from the low level excitor setting, the rotor will be exposed to much more current. Motor start ups usually last 15 to 17 secs.
What things we should look at if we don't want to have a dynamic simulation conducted? Excitation system manufacturer is confident these settings which he is proposing are correct.
Has anyone done anything similar at any site? What were the basis? and what were the checks done before the change?
Sincerely,
MRasool