Ok,Всем привет. Что вы думаете? Почему Temp.Match не работает до конца? The temperature stopped GT Exhaust Temp 461-463°с and did not rise anymore.
Your description of the event/situation is not well clear...холодный пуск - паровая турбина. Gas turbine- 7MWT at mode Temp.Match. Еxhaust gas temperature- Started at 371 degrees and stopped at 461 degrees.waited 3 hours.but the temperature did not rise anymore
HiHI everybody,
Is theere anybody who can share information about temperature matching function or have detailed description of this function? For 6FA units (Mark VIe TMR)
Here some notes from OEM manuals:Hi
Here is some notes interesting on "Temperature matching mode":
The second mode is the temperature matching mode. In this mode, the exhausted gas
temperature is controlled according to a temperature reference signal whereas the load is
maintained to a minimal value (typically 8%). Usually, the goal of the regulation is to
maintain the GT outlet exhausts temperature constant (equal to the nominal value, in
order to optimize the efficiency of the HRSG and of the whole plant).
I am sure it can help to enghlight some points you are looking for...
As every units got his own appcode , without be able to check this program ,I cannot add more comments..
ControlsGuy25.
Does this function need if you don't use HRSG , or it can be useful,if you are working in simplecycle?
Hi,Hi everybody, especially I am interested in work principal of this function, before start up unit, I need activate this function, don't I? And of may be is there anybody here who knows what the set setpoints are?
For simple cycle Iam not sure that this mode is selected ...It can be in case of Process steam or such as add on mode , from HRSG..Does this function need if you don't use HRSG , or it can be useful,if you are working in simplecycle?
Thread starter | Similar threads | Forum | Replies | Date |
---|---|---|---|---|
D | Omron e5ax temp controller repair | General Automation Chat | 2 | |
K | UDC 3000 temp reading | Process Control | 4 | |
Sending Temp. setpoint via BACnet to a boiler | Programmable Logic Controller - PLC | 2 | ||
M | over temp trip in frame 6 mark 5 gas turbine | Power Generation | 9 | |
J | Temp match shutdown ? | Power Generation | 3 |