Thank you for supplying such a well-reasoned and detailed reply.
Specifically, ZubairKhan, let’s say a single 25MW three-phase synchronous generator driven by a combustion turbine was operating at rated frequency (rated speed) and at 11kV and supplying a load of mostly induction motors driving pumps and fans and conveyor belts, small transformers driving lights (a mix of fluorescent, incandescent and LED) and smaller motors and air conditioning units (more induction motors). There are also a few tea kettles and some computers and computer monitors. Finally the “house load” of the combustion turbine auxiliaries is also being powered by this unit. It is being operated in Isochronous Speed Control mode independent of any other synchronous generator. The total load on the machine at this instant is approximately 5.0 MW.
How would you change the load on the machine in question from 5.0MW to 19.7MW by changing the voltage and current supplied to the generator?
Further, let’s say in a more realistic setting the same machine is synchronized to a grid with tens of other machines all operating at rated frequency (rated speed) and this machine is producing 5.0 MW of a total load of 3,467 MW. It is being operated in Droop Speed Control mode. How would you increase the load of this machine from 5.0MW to 20.2MW by changing the voltage and current supplied to the machine? How much would you have to increase the voltage and current supplied to the generator, in percentage of rated voltage and current?
It would probably surprise you to learn that every minute of every day there are hundreds of ill-trained people operating synchronous generators all around the world. A lot of the reason for this is the automation (control system). A good portion of the reason is that owners don’t want to pay for proper training and governments don’t have regulations/laws mandating certification for power plant operators and so owner believe they don’t have to invest in training or pay to acquire trained, experienced employees to operate the equipment. So, your statement about proper training and experience to mitigate risk is also without much merit in many places in the world (including some very modern and industrialized nations). The only training some people receive is OJT: On the Job Training. And a lot of that is given by people who got their knowledge and experience from OJT. (Sometimes OJT is good, but most often it’s lacking, sometimes severely lacking.) And it’s the automation that prevents a lot of catastrophes and serious injuries and deaths.
But, getting back to the questions you didn’t answer and are unresolved; How does one change the load (watts; kW; MW) of a synchronous generator by changing the voltage and current supplied to the generator and how much would one have to change that voltage and current to affect a change of approximately 60% of the rated load of the machine?
Seriously, I am trying to learn something from you since you stated that was how (or at least one way) to increase the load of a synchronous generator on planet earth in our solar system driven by prime movers (turbines and reciprocating engines). I know another way, and it’s the only one I know, but if there’s another way (or maybe more?) I would like to learn.
I’m an old fart, but I am still learning new things every day. A new language (it’s a great way to keep one’s mind active and engaged), new procedures, new culture, new foods, new ways of growing foods, and new perspectives as well as different methods and materials for construction. This would be something to keep my mind engaged and active as I try to grasp the concept(s) and principles. So, help a fellow out and explain it to me, please.
Thanks!
Specifically, ZubairKhan, let’s say a single 25MW three-phase synchronous generator driven by a combustion turbine was operating at rated frequency (rated speed) and at 11kV and supplying a load of mostly induction motors driving pumps and fans and conveyor belts, small transformers driving lights (a mix of fluorescent, incandescent and LED) and smaller motors and air conditioning units (more induction motors). There are also a few tea kettles and some computers and computer monitors. Finally the “house load” of the combustion turbine auxiliaries is also being powered by this unit. It is being operated in Isochronous Speed Control mode independent of any other synchronous generator. The total load on the machine at this instant is approximately 5.0 MW.
How would you change the load on the machine in question from 5.0MW to 19.7MW by changing the voltage and current supplied to the generator?
Further, let’s say in a more realistic setting the same machine is synchronized to a grid with tens of other machines all operating at rated frequency (rated speed) and this machine is producing 5.0 MW of a total load of 3,467 MW. It is being operated in Droop Speed Control mode. How would you increase the load of this machine from 5.0MW to 20.2MW by changing the voltage and current supplied to the machine? How much would you have to increase the voltage and current supplied to the generator, in percentage of rated voltage and current?
It would probably surprise you to learn that every minute of every day there are hundreds of ill-trained people operating synchronous generators all around the world. A lot of the reason for this is the automation (control system). A good portion of the reason is that owners don’t want to pay for proper training and governments don’t have regulations/laws mandating certification for power plant operators and so owner believe they don’t have to invest in training or pay to acquire trained, experienced employees to operate the equipment. So, your statement about proper training and experience to mitigate risk is also without much merit in many places in the world (including some very modern and industrialized nations). The only training some people receive is OJT: On the Job Training. And a lot of that is given by people who got their knowledge and experience from OJT. (Sometimes OJT is good, but most often it’s lacking, sometimes severely lacking.) And it’s the automation that prevents a lot of catastrophes and serious injuries and deaths.
But, getting back to the questions you didn’t answer and are unresolved; How does one change the load (watts; kW; MW) of a synchronous generator by changing the voltage and current supplied to the generator and how much would one have to change that voltage and current to affect a change of approximately 60% of the rated load of the machine?
Seriously, I am trying to learn something from you since you stated that was how (or at least one way) to increase the load of a synchronous generator on planet earth in our solar system driven by prime movers (turbines and reciprocating engines). I know another way, and it’s the only one I know, but if there’s another way (or maybe more?) I would like to learn.
I’m an old fart, but I am still learning new things every day. A new language (it’s a great way to keep one’s mind active and engaged), new procedures, new culture, new foods, new ways of growing foods, and new perspectives as well as different methods and materials for construction. This would be something to keep my mind engaged and active as I try to grasp the concept(s) and principles. So, help a fellow out and explain it to me, please.
Thanks!