The operator screen says the tank is at 47 %, just under setpoint, and steady. Out in the plant the level is 4.3 m and climbing. The high alarm stays silent.
That is the scenario in the first episode of our new series, "How OT actually works". We take one control loop apart: transmitter, PID controller, control valve. The tank (T-101) and every number in it are a hypothetical teaching example.
What the video walks through:
Why a forged level drives the tank up. A PV held just below setpoint makes the controller's integral action wind the output down until the outlet valve is shut.
An alarm calculated from the transmitter that controls the tank isn't a second opinion. It's the same opinion twice.
4–20 mA live zero catches broken wires, not lies. 11.5 mA from a forged signal looks exactly like 11.5 mA from a healthy transmitter.
Siemens S7-1500 PID_Compact defaults, from the Siemens PID control function manual (09/2016 edition; check yours):
Why the last layer should be an independent high-high trip that doesn't come through the screen.
It ends with a read-only "walk one loop" checklist. Any change goes through MOC with the process owner.
Sources: NIST SP 800-82 Rev. 3, MITRE ATT&CK for ICS, Siemens manuals, and T. Kuphaldt's Lessons In Industrial Instrumentation (CC BY 4.0).
Watch:
#OTsecurity #ICS #ProcessControl #Instrumentation #SCADA #PLC"
That is the scenario in the first episode of our new series, "How OT actually works". We take one control loop apart: transmitter, PID controller, control valve. The tank (T-101) and every number in it are a hypothetical teaching example.
What the video walks through:
Why a forged level drives the tank up. A PV held just below setpoint makes the controller's integral action wind the output down until the outlet valve is shut.
An alarm calculated from the transmitter that controls the tank isn't a second opinion. It's the same opinion twice.
4–20 mA live zero catches broken wires, not lies. 11.5 mA from a forged signal looks exactly like 11.5 mA from a healthy transmitter.
Siemens S7-1500 PID_Compact defaults, from the Siemens PID control function manual (09/2016 edition; check yours):
- Setpoint limits fall back to the PV limits of 0–120 %, so a setpoint above the top of the tank is accepted.
- With the default ActivateRecoverMode, a PV-limit error leaves the loop in automatic. Siemens itself warns this can damage the system.
- An invalid raw input drives the output to a substitute value, which defaults to 0.0.
- a forced input (on an S7-1500 the force job is stored on the memory card and shown on the CPU display);
- a write over the network, which depends on the CPU's access settings;
- injection at the marshalling cabinet.
Why the last layer should be an independent high-high trip that doesn't come through the screen.
It ends with a read-only "walk one loop" checklist. Any change goes through MOC with the process owner.
Sources: NIST SP 800-82 Rev. 3, MITRE ATT&CK for ICS, Siemens manuals, and T. Kuphaldt's Lessons In Industrial Instrumentation (CC BY 4.0).