iFix OPC server and Siemens S-400 system

  • Thread starter Birgir Sigurthorsson
  • Start date
B

Thread Starter

Birgir Sigurthorsson

Does anyone have application notes how to configure Siemens S7-400 redundant system with
iFix OPC server verion 7.XXX driver?
 
R

Raymond van der Tas

To give your OPC Client a transparent method for connecting to either the primary or the backup PLC you could install an OPC aggregation product like DataWorX32. First you would create two channels "Primary" and "Backup" in your OPC Server. The address space below the primary and backup plc will have to be identical. Then add a Switch Alias named "PLC" in DataWorX32. The switch alias would be given two values "OPCSvr_Logical_Prog_ID\Primary" and "OPCSvr_Logical_Prog_ID\Backup"
The condition for having the switch switch between the primary or backup PLC can be configured based on for instance the quality of an OPC tags.

Finally your OPC client can connect to the PLC pair as if it is only one. The tag syntax of an OPC tag would look similar to
ICONICS.DataWorX32.1\[[PLC]].Temperature

For downloading a free version
http://www.iconics.com/support/free_demos.asp

Regards
Raymond van der Tas
 
J

John Barnet Engineering

It does not work. You need S7-Redconnect software and you have to have an OPC Client that can support redundancy, iFix cannot do it.
 