I am currently on a platform with a Thommasen.B.V FR6B following an MI service. For years they have had an on going issue with the Immersion heater tripping the starter cubicle on the heaters own internal thermostat 49QT after only 20-40sec operation. It is now never used and the same remedial action has always been to just try changing the heater again and again.
On a previous visit back in 2017 I enquired on this website for a GE TIL 1428-3 that described a mod to change the electrical termination linkage from Delta to Star thereby reducing the output from 15KW to 5KW. This was carried out at the time but the heater still continued to trip but maybe after a slightly longer time of operation.
As the heater here can be removed from a thermowell in the tank it is in effect I would say rather a space heater, heating the air space rather than in direct contact with the oil medium. All of the drawings describe this an immersion heater rather than a space heater. I have now been coming to the conclusion that the heater is tripping because the coils are not immersed and it is overheating as it is not being used as designed. But then I read some past threads here and this conclusion is contradicted and indeed the heaters are normally inserted into a well for ease of replacement.
As the units I visit are normally operational I have never really had the opportunity to see an empty lube oil tank and how the heater is found in the tank so now questioning if some units have a thermowell and others don't. for different manufacturers
Could anyone advise on clarifying whether
a) that the normal configuration for the immersion heater is indeed to be inserted into a thermowell for ease of replacement and to prevent having to drain tanks
b) that the description as an "Immersion heater" is really not correct as the heater coils are not normally immersed at all.
c) Whether the type of heater required needs to be specific to operating in an air pocket.
Have got myself in a twist on now thinking that the heater coils have to immersed in the lube oil for proper heat convection to prevent coil overheating, but then realise the tank would have to be drained every time you had a faulty heater which would make no sense.
I would add that electrically the MCC starter and thermostats etc have all been checked many times and that the same 49QT thernostat tripping action also occurs on the platforms other FR6B.
Thanks for any comments
On a previous visit back in 2017 I enquired on this website for a GE TIL 1428-3 that described a mod to change the electrical termination linkage from Delta to Star thereby reducing the output from 15KW to 5KW. This was carried out at the time but the heater still continued to trip but maybe after a slightly longer time of operation.
As the heater here can be removed from a thermowell in the tank it is in effect I would say rather a space heater, heating the air space rather than in direct contact with the oil medium. All of the drawings describe this an immersion heater rather than a space heater. I have now been coming to the conclusion that the heater is tripping because the coils are not immersed and it is overheating as it is not being used as designed. But then I read some past threads here and this conclusion is contradicted and indeed the heaters are normally inserted into a well for ease of replacement.
As the units I visit are normally operational I have never really had the opportunity to see an empty lube oil tank and how the heater is found in the tank so now questioning if some units have a thermowell and others don't. for different manufacturers
Could anyone advise on clarifying whether
a) that the normal configuration for the immersion heater is indeed to be inserted into a thermowell for ease of replacement and to prevent having to drain tanks
b) that the description as an "Immersion heater" is really not correct as the heater coils are not normally immersed at all.
c) Whether the type of heater required needs to be specific to operating in an air pocket.
Have got myself in a twist on now thinking that the heater coils have to immersed in the lube oil for proper heat convection to prevent coil overheating, but then realise the tank would have to be drained every time you had a faulty heater which would make no sense.
I would add that electrically the MCC starter and thermostats etc have all been checked many times and that the same 49QT thernostat tripping action also occurs on the platforms other FR6B.
Thanks for any comments
Attachments
-
332 KB Views: 13