B
BruceD
> Almost all textbooks assume certain parameters to be constant, eg. terminal voltage, excitation,
> shaft speed, synchronous reactance, etc. in order to represent phasor diagrams.... but in
> the real world this is not so.
Most phasor diagrams use per unit values, in which everything is expressed in terms of the terminal voltage as 1. The synchronous reactance is the voltage drop in the windings at rated current.
In your case, the reactance can be treated as approximately proportional to speed or frequency. So if speed increases by 5 %, the synchronous reactance will also increase by 5 %.
I would suggest you start with the machine at rated conditions, and find the internal emf in per unit terms assuming a terminal voltage of 1 pu. Now, multiply this value by 1 factor to give the effect of speed (1.05 if speed is raised by 5 %) and another to give the effect of excitation current (1.05 if excitation is increased by 5%). Change the reactance in proportion to the change in speed.
This will give a simple voltage - reactance - resistance circuit that can be handled in the usual way to find the load current.
For a PM generator, you can forget (to a 1st approximation) the effect of field current.
> shaft speed, synchronous reactance, etc. in order to represent phasor diagrams.... but in
> the real world this is not so.
Most phasor diagrams use per unit values, in which everything is expressed in terms of the terminal voltage as 1. The synchronous reactance is the voltage drop in the windings at rated current.
In your case, the reactance can be treated as approximately proportional to speed or frequency. So if speed increases by 5 %, the synchronous reactance will also increase by 5 %.
I would suggest you start with the machine at rated conditions, and find the internal emf in per unit terms assuming a terminal voltage of 1 pu. Now, multiply this value by 1 factor to give the effect of speed (1.05 if speed is raised by 5 %) and another to give the effect of excitation current (1.05 if excitation is increased by 5%). Change the reactance in proportion to the change in speed.
This will give a simple voltage - reactance - resistance circuit that can be handled in the usual way to find the load current.
For a PM generator, you can forget (to a 1st approximation) the effect of field current.