First of all, thanks for your detailed reply, it was very intersting and I think I got my answer....But to be sure, I am trying to find the right IGV position in a simulation software, so consider following picture (its section view of just one IGV blade, the rest of blades will be replicated around the rotor axis) : Based on your explanation I think IGV is measured with the angle I shown, am I right?@AminTabei,
I don't know if I really understand the question you are asking, so I'm going to describe the IGVs and how their position is relates to the air flow into the machine, and then method by which GE-design heavy duty gas turbines monitor IGV position (angle).
IGVs are curved devices (air foils). But their position is relative to whether or not those curved devices are parallel to the axis of air flow into the axial compressor of a combustion turbine. If IGVs could be moved to a position of 0 DGA (DeGrees Angle)--with they cannot be--they would be perpendicular to the air flow into the machine--in effect stopping the flow of air into the machine. If IGVs could be moved to a position of 90 DGA they would be parallel to the flow of air into the machine, in effect permitting maximum air flow into the axial compressor of the machine. (There are mechanical stops that prevent the closure of the IGVs of many GE-design heavy duty gas turbines below approximately 32 DGA and above approximately 88 DGA (some machines have slightly larger operating ranges, say 30 to 90 DGA).
The IGV hydraulic actuator has two (2) LVDTs (Linear Variable Differential Transformers) attached to it. As the hydraulic actuator extends or retracts there are rods (called cores) that move inside a stationary set of coils (called armatures). One set of coils is powered by (excited) the Mark* turbine control system. As the hydraulic actuator piston and rod moves up and down to open and close the IGVs the LVDT cores move up and down inside the stationary coils and the voltage developed on the second set of coils changes (varies). This voltage is connected to the Mark* turbine control system. The LVDT output voltage changes with the position of the cores inside the stationary armatures as the actuator rod moves to change the IGV angle.
The LVDT output voltage is linear--meaning the voltage varies by the same amount as the core moves up and down inside the armature. For example (this is ONLY an example!), a movement of 13mm (approximately 0.5 inch) might cause the LVDT output voltage to change by 0.7 V AC RMS. Each movement of 13mm causes the output to change by 0.7 VAC RMS--meaning the LVDT output voltage is linear with respect to movement. (And each movement of 13mm might cause the IGVs to move by approximately 15 DGA (DeGrees Angle).
This means that to make the IGV position measurement reflect the ACTUAL physical position of the IGVs the LVDT output voltage that is connected to the Mark* turbine control panel must be "calibrated"--because there can be differences in LVDT output voltages for any given IGV position between not only individual LVDTs on the IGV hydraulic actuator but between machines. It's important to ACCURATELY calibrate the LVDT output voltage to the ACTUAL physical position of the IGVs. This is done using the calibration feature of the Mark* AND should (must, really) be verified using a machinist's protractor (or a similar tool/method).
The beauty of LVDTs as position measurement devices is:
1) They are capable of prolonged operation in high-temperature environments and low-temperature environments
2) They are capable of prolonged operation in high-vibration environments
3) The output voltages DO NOT drift (change) over time
4) There is only one moving part, and when properly installed and maintained, there is no contact between the moving part and the stationary part.
(The above reasons are why LVDTs are used on aircraft to measure flap angle and elevator angle AND on rocket motors--they are simple, rugged devices and their output does not drift (change) over time like so many other types of position-measuring devices. Far too many people have the idea that LVDT output voltage versus position can change over time--which is nearly impossible to do)--and so they think the answer to every perceived problem which be remotely attributed to the IGVs requires "calibration" of the LVDT feedback voltage to the Mark*, which usually ends up resulting in more problems than it might have solved. BEFORE any LVDT feedback is "calibrated" it should FIRST be checked by positioning the IGVs and measuring the position and comparing it to the IGV position on the HMI screen to determine if the output has drifted/changed and requires recalibration. AND, if the output has indeed changed then some further investigation should be performed as to why it has changed (some mechanical problem most likely) and resolve that issue before "calibrating." Have you ever known a passenger jet to have to recalibrate their flap angles mid-flight??? LVDTs are very reliable devices. Many of those same people who think LVDT output voltage can and does drift/change over time requiring calibration also believe that using the calibration feature of the Mark* turbine control system somehow magically affects the electro-hydraulic servo valve used to cause the IGV actuator to open and close--which is ABSOLUTLEY NOT TRUE--and so they think they are getting a "two-fer" (two results for a single action) by calibrating the IGVs or the fuel control valves whenever there is some kind of problem (real or perceived).)
Anyway, I hope I have answered your "question." You can refer to the Operation and Maintenance Manuals provided with GE-design heavy duty gas turbines for pictures and brief descriptions of operation, or if you require clarification, you can write back with a better description of what you're asking.