Interfacing WW with PI over serial

S

Thread Starter

Steve Winter

OSIsoft basically says NO WAY MAN but being a real jerk myself I don't believe a simple NO is the final answer.

Has anyone out there done or attempted something similar???

The basic NERC standard to ANY non-routable point to point comm line is acceptable. My initial thought was to use a PPP Serial connection between the PI server and the Wonderware endpoint..

Any thoughts
 
S

Steve Winter

We're quickly coming to that conclusion, I was hoping there might be a solution that would not require us to add more machines and more interfaces.

One of my engineers came up with a Rube Goldburg thing using stripped down network drivers with NWLINK only that will pass DDE but not be layer 3 routable. Any thoughts??

Thanks for your reply.

Steve
 
Making this work over a serial link would be a real science project. However, I do not believe NERC requires connections to be non-routable.

In fact, every vendor of whom I am aware is using TCP/IP over Ethernet in power plants. There ARE blocks of IP addresses that are non-routable.

Perhaps all you need to do is VLAN this connection on a non-routable network (e.g. 192.168.n.n)
 