After a trip on "compressor operating limit max control error". unit is not starting up on liquid fuel and trip each time on loss of flame.
Activities performed: checked pressure upstream liquid fuel stop valve ok at 50psi. checked pressure on atomizing air booster line around 6 to 7 psi at startup, replaced flow divider, liquid fuel check valves and finally liquid fuel bypass is responding. despite all this during startup unit still tripping on loss of flame. can anybody advise on the issue unit is now running on gas fuel.
Activities performed: checked pressure upstream liquid fuel stop valve ok at 50psi. checked pressure on atomizing air booster line around 6 to 7 psi at startup, replaced flow divider, liquid fuel check valves and finally liquid fuel bypass is responding. despite all this during startup unit still tripping on loss of flame. can anybody advise on the issue unit is now running on gas fuel.