Can you use your Bentley software(System 1) to get the trend from the keyphasor speed compare to all your speed inputs on the low speed shaft, they should be in your trip log. I believe if the safeset had sheared you would be getting zero generator speed. Likely it looks like a faulty key phasorThe VG issues is due to failed bushings in the IGV. The whole IGV will be replaced in the fall of 2024. The main issue we are attempting to address is the "Generator Safeset Failure" as that is what causing the unit to shut down.
We have basically tracked it down to the possibility of one of the NSD LP Rotor Sensors. We are waiting for the lock out to clear right now and will go into a crack to see if we find any difference in NSDA vs NSDB.
This failed on start up.. The first time we were at 5mw and it just shut down. The second time we just hit the wire and it shut down. The third time we set a trend up to monitor the items on the A_ESD page and went for a start, we did not even get to activate the sync before it shutdown and went directly to a 4hr lockout.
Sam