hi CSA,
the configuration of regulator1 SRV is:
reg type: 2_LVpsMAX
RegGain: 1.8
RegNulbias 2.67
Dither Amp 2.0
Dither Freq 100.0hz
LVDT1input LVDT1
LVDT2input LVDT2
MnLVDT1_vms 1.033185 1.027448 1.031891
MxLVDT1_vms 3.563585 3.544263 3.559962
MnLVDT2_vms 1.033733 1.032113 1.032384
MxLVDT2_vms 3.475117 3.49347 3.470385
LVDT Margin 5.0
TMR_difflimit 5.0
and for GCV regulator
eg type: 2_LVpsMAX
RegGain: 1.8
RegNulbias 2.67
Dither Amp 2.0
minposvalue 0.0
Maxposvalue 100.0
Dither Freq 100.0hz
LVDT1input LVDT10
LVDT2input LVDT11
MnLVDT1_vms 0.546242 0.543745 0.54634
MxLVDT1_vms 3.354269 3.337259 3.350151
MnLVDT2_vms 0.579185 0.581698 0.576747
MxLVDT2_vms 3.369209 3.384762 3.354698
LVDT Margin 5.0
TMR_difflimit 5.0
so mechanical the valve is open and close when i stoke the valve but for regulator configuration is like this. so no mechanical problem ,
for Control Constant:
FPKGSD: -25% SRV SHUT DOWN COMMAND
FRKCRMN 0% SRV REFERENCE MINIMUM VALUE
FRKCRMX 100% SRV REFERENCE MAXIMUM VALUE
K30FSRSU_T2S:0s Sliding FSR t2 SRV closing early
time
K3GRVA 3s SRV not following alarm time delay
K3GRVAX 3% SRV not following alarm set point
K3GRVT 5S SRV not following trip time delay
K3GRVTX 5% SRV not following trip set point
LK3GRVFB -6.67% SRV VALVE POSITION TROUBLE
SETPOINT
LK3GRVFLTD 2s SRV VALVE TROUBLE ALARM DELAY
LK3GRVO 6.67% SRV VALVE OPEN TROUBLE SETPOINT
LK3GRVSC 30% SRV VALVE SERVO CURRENT TROUBLE
SETPOINT
LK60FSGH 9% HIGH SRV STROKE REFERENCE SETPOINT
SO ALL CONFIGURATION IS LIKE THESE
Can you CSA please help me
now the turbine is running
SRV lvdt= 64.4 valve actuation= -3.07
GCV lvdt= 45.65 valve actuation= -0.26
the configuration of regulator1 SRV is:
reg type: 2_LVpsMAX
RegGain: 1.8
RegNulbias 2.67
Dither Amp 2.0
Dither Freq 100.0hz
LVDT1input LVDT1
LVDT2input LVDT2
MnLVDT1_vms 1.033185 1.027448 1.031891
MxLVDT1_vms 3.563585 3.544263 3.559962
MnLVDT2_vms 1.033733 1.032113 1.032384
MxLVDT2_vms 3.475117 3.49347 3.470385
LVDT Margin 5.0
TMR_difflimit 5.0
and for GCV regulator
eg type: 2_LVpsMAX
RegGain: 1.8
RegNulbias 2.67
Dither Amp 2.0
minposvalue 0.0
Maxposvalue 100.0
Dither Freq 100.0hz
LVDT1input LVDT10
LVDT2input LVDT11
MnLVDT1_vms 0.546242 0.543745 0.54634
MxLVDT1_vms 3.354269 3.337259 3.350151
MnLVDT2_vms 0.579185 0.581698 0.576747
MxLVDT2_vms 3.369209 3.384762 3.354698
LVDT Margin 5.0
TMR_difflimit 5.0
so mechanical the valve is open and close when i stoke the valve but for regulator configuration is like this. so no mechanical problem ,
for Control Constant:
FPKGSD: -25% SRV SHUT DOWN COMMAND
FRKCRMN 0% SRV REFERENCE MINIMUM VALUE
FRKCRMX 100% SRV REFERENCE MAXIMUM VALUE
K30FSRSU_T2S:0s Sliding FSR t2 SRV closing early
time
K3GRVA 3s SRV not following alarm time delay
K3GRVAX 3% SRV not following alarm set point
K3GRVT 5S SRV not following trip time delay
K3GRVTX 5% SRV not following trip set point
LK3GRVFB -6.67% SRV VALVE POSITION TROUBLE
SETPOINT
LK3GRVFLTD 2s SRV VALVE TROUBLE ALARM DELAY
LK3GRVO 6.67% SRV VALVE OPEN TROUBLE SETPOINT
LK3GRVSC 30% SRV VALVE SERVO CURRENT TROUBLE
SETPOINT
LK60FSGH 9% HIGH SRV STROKE REFERENCE SETPOINT
SO ALL CONFIGURATION IS LIKE THESE
Can you CSA please help me
now the turbine is running
SRV lvdt= 64.4 valve actuation= -3.07
GCV lvdt= 45.65 valve actuation= -0.26