Mark IV vibration control constant calculation

C

Thread Starter

chitti babu

How to calculate metrix make siesmic vibration sensor sensitivity gain control constant CAK39V1 in mark 4 gas turbine control panel.

Sensitivity of metrix sensor is 150mv/inch/sec.

thanks in advance.
 
The method for handling different sensitivities changed during the product life of the Mark IV. It wasn't possible on early Mark IV panels; it was difficult at best on later panels.

The Control Specification - System Settings document should provide some information if it's possible on the panel at your site. I think the vibration protection information is covered in Sect. 09 of the Control Specification.

Sometimes, the Control Specification - System Adjustments had some relevant information, also.

Wish the news was better. Perhaps someone reading this post who has a Mark IV with the Control Constant name you listed and with 150 mv/IPS sensors could provide the value of the Control Constant.
 