D
All
We have 2 x Mark V panels (GT and ST) + 2 nos. HMI (Windows NT 4.0 based running Cimplicity 4.0). The GT HMI is acting as a Master Time Keeper ie. installed with PCI-card connected to a GPS module and supposedly "broadcast" a time signal to everyone in the Arcnet Stagelink network.
At the moment, Mark V panels and both HMIs having different timestamp (3 different times)
Below is the F:\TIMESYNC.DAT output:<pre>
******** GT HMI (TIMESYNC MASTER) ********
TIMESYNC HIGHRES
LOCAL_TIMESET ENABLED
TIME_LOAD LOCAL
I_TIME UTC
MARKV_TIME UTC
******** ST HMI (TIMESYNC SLAVE) ********
TIMESYNC SLAVE
LOCAL_TIMESET ENABLED
TIME_LOAD NETWORK
I_TIME UTC
MARKV_TIME UTC</pre>
Can someone shed some light? According to GEH-6126, there’s no such setting as "TIMESYNC HIGHRES". The syntax is TIMESYNC <controller> MODE <mode> [LEVEL_SHIFT]