Namatimangan08
Think about this. All (almost) prime movers can have both primary and secondary control. At any time the governor should respond to only one type of control, either primary or secondary. Not both. To make thing worse both controls take system frequency as one of the inputs.
Assuming your prime mover has both type of controls. You want your prime mover to operate under AGC- Constant frequency. Obviously you don't want your prime mover to operate under droop mode. How you are going to "tell" the controller?
About 15 years ago, it was achieved by making separation based on frequency dead band. Within this dead band, say 49.85 -50.15 Hz (Constant frequency regulation band), the droop response was disabled. The prime mover was under AGC-Constant frequency's command. In case the actual frequency felt outside this range, AGC suspended. Droop response took over.
Honestly, I don't know of much if any advancement in this area today.
Assuming your prime mover has both type of controls. You want your prime mover to operate under AGC- Constant frequency. Obviously you don't want your prime mover to operate under droop mode. How you are going to "tell" the controller?
About 15 years ago, it was achieved by making separation based on frequency dead band. Within this dead band, say 49.85 -50.15 Hz (Constant frequency regulation band), the droop response was disabled. The prime mover was under AGC-Constant frequency's command. In case the actual frequency felt outside this range, AGC suspended. Droop response took over.
Honestly, I don't know of much if any advancement in this area today.