The IDOS MarkV (TMR) of one of our Frame 6B GTs (T4) seems very strange from last few years (from 2021 may be). Last time when we replaced <R> TCEA and TCDA with same EEPROMs (due to DCC IO CARD OBJ#4 and OBJ#15 reset with so many input and out diagnostic alarms), all got A7 status. Then everything was fine. From last week we faced the same thing again in <R> and <S> both at standby condition of the same unit. Replaced IONET cable, everything came back to A7 status. But the problem came back on the next day!!! For test purpose We picked both TCEA and TCDA of R and S and installed to another Unit T3 (Standby), T3 behaved normal!!! Why this is happening?
Note: Measured voltages at test points of each core TCPS, DCC, TCEA, and found all normal.