Modbus Poll to ABB REX640 relay

What are the IP addresses of your computer running Modbus Poll and of the REX640?

Can you show a screenshot of your Modbus Poll settings?

Are you seeing any errors in Modbus Poll?
 
Are you making a direct connection between your computer and the REX640 (i.e. just an Ethernet cable connecting the two) or are you using an Ethernet switch (potentially with other devices on the network)?

If it's the latter, does the ping still work if you disconnect the REX640 from the network? If so, you have duplicate IP addresses on your network and need to change the REX640 to an unused IP.

Otherwise, it seems Modbus/TCP is not actually enabled on the REX640. Note that some devices require a power cycle for new communication settings to take effect. So if you haven't done so already, try power cycling the REX640.
 
Are you making a direct connection between your computer and the REX640 (i.e. just an Ethernet cable connecting the two) or are you using an Ethernet switch (potentially with other devices on the network)?

If it's the latter, does the ping still work if you disconnect the REX640 from the network? If so, you have duplicate IP addresses on your network and need to change the REX640 to an unused IP.

Otherwise, it seems Modbus/TCP is not actually enabled on the REX640. Note that some devices require a power cycle for new communication settings to take effect. So if you haven't done so already, try power cycling the REX640.
Are you making a direct connection between your computer and the REX640 (i.e. just an Ethernet cable connecting the two) or are you using an Ethernet switch (potentially with other devices on the network)? - using ethernet cable connecting my pc and the relay.

If it's the latter, does the ping still work if you disconnect the REX640 from the network? If so, you have duplicate IP addresses on your network and need to change the REX640 to an unused IP. - I'll try this one

Otherwise, it seems Modbus/TCP is not actually enabled on the REX640. Note that some devices require a power cycle for new communication settings to take effect. So if you haven't done so already, try power cycling the REX640. - there's a possibility that it's not enabled.

Thank you, I'll try your suggestion once I returned to site and be able to access the REX640. I'll give you feedback once I tried.

Thank you very much.
 
The STATUS would be expected to be false because we already know you are unable to establish a connection. The end goal is to establish a connection, and in turn, the STATUS will show true. But we need to figure out why the connection is not succeeding.

What do the "CnReject no sockets" and "CnReject unregistered" counters show?
 
The STATUS would be expected to be false because we already know you are unable to establish a connection. The end goal is to establish a connection, and in turn, the STATUS will show true. But we need to figure out why the connection is not succeeding.

What do the "CnReject no sockets" and "CnReject unregistered" counters show?
Both shows -1.. does it mean that the modbus protocol is not configured?

1756861718592.png
 
I'm not sure what the -1 value means. If I were to guess, it may just be the value that all counters are initialized to, indicating counting has not begun.

From your screenshots it seems that you have configured Modbus Slave Port 1 and are using Ethernet TCP 1. Does this device have multiple Ethernet ports (either physical or virtual)? Perhaps you configured the wrong port? For example, is there a Modbus Slave Port 0 or Modbus Slave Port 2?

Also, just to double check, did power cycling not make any difference?

Does this device have a built-in web page that you can access? If you also can't access its web page (assuming it has one), there may be some other, higher level settings that need to be modified.
 
I'm not sure what the -1 value means. If I were to guess, it may just be the value that all counters are initialized to, indicating counting has not begun.

From your screenshots it seems that you have configured Modbus Slave Port 1 and are using Ethernet TCP 1. Does this device have multiple Ethernet ports (either physical or virtual)? Perhaps you configured the wrong port? For example, is there a Modbus Slave Port 0 or Modbus Slave Port 2? - I'll check this on site tomorrow

Also, just to double check, did power cycling not make any difference? - It did not make any difference

Does this device have a built-in web page that you can access? If you also can't access its web page (assuming it has one), there may be some other, higher level settings that need to be modified. - The web page is accessible
Thank you very much.
 
Thank you very much.
I'm not sure what the -1 value means. If I were to guess, it may just be the value that all counters are initialized to, indicating counting has not begun.

From your screenshots it seems that you have configured Modbus Slave Port 1 and are using Ethernet TCP 1. Does this device have multiple Ethernet ports (either physical or virtual)? Perhaps you configured the wrong port? For example, is there a Modbus Slave Port 0 or Modbus Slave Port 2?

Also, just to double check, did power cycling not make any difference?

Does this device have a built-in web page that you can access? If you also can't access its web page (assuming it has one), there may be some other, higher level settings that need to be modified.
Hi,

I was on the wrong ethernet port, so now I'm connected. The issue now is the modbus address. I see the address in the modbus, but how can I use this address to create a driver so that I can remotely operate the REX640 and know its status.
Also how to know the address in the rex640's equivalent to modbos poll address?

1756948809258.png1756948908639.png
 
For that, you will need to read and understand all of section 3.4 Modbus application data in the REX640 Modbus manual that I linked previously:
https://library.e.abb.com/public/c0...1OOuHaPPeKV/+AIrDsvHg3gkSOcp4pZwhyysADG38yoyH

This device seems to be quite complicated in that all data is freely mappable to Modbus, so it seems you either need to create a mapping yourself using ABB's software or select a pre-configured mapping (if that exists). I would encourage you to contact ABB's technical support if you still don't understand the Modbus mapping for this device, as this goes above and beyond general Modbus advice that we can offer here.

Perhaps there is another member familiar with the REX640 and its Modbus functionality that will chime in and provide guidance, but I think your best bet would be to contact ABB directly.
 
For that, you will need to read and understand all of section 3.4 Modbus application data in the REX640 Modbus manual that I linked previously:
https://library.e.abb.com/public/c0...1OOuHaPPeKV/+AIrDsvHg3gkSOcp4pZwhyysADG38yoyH

This device seems to be quite complicated in that all data is freely mappable to Modbus, so it seems you either need to create a mapping yourself using ABB's software or select a pre-configured mapping (if that exists). I would encourage you to contact ABB's technical support if you still don't understand the Modbus mapping for this device, as this goes above and beyond general Modbus advice that we can offer here.

Perhaps there is another member familiar with the REX640 and its Modbus functionality that will chime in and provide guidance, but I think your best bet would be to contact ABB directly.
Hi,

Thank you very much, I wouldn't have known that I may be in the wrong ethernet port without your assistance.
 