The longest distance supported by the serial communications is 100ft, normally that value applies on RS232. If you are using 485 distances between 10 & 20 ft, it's your answer.
i had work with mod bus rtu protocol using rs 485. i didn't calculate the distance, but the system is working perfectly with seven individual panels connected to a remote scada via modbus..may be the distance between the panels will be around 1200 meters..
I suspect RS-485 will work at longer distances than the usually cited maximum 1200m (at low baud rates) from 2 different farther-than-the-spec non-485 experiences.
One experience involved a half duplex, no handshake 3 wire (Rx,Tx, Gnd) RS-232 link with the usual 50ft (15m) distance limitation. The plant "electrician" had run 200ft (60m) of 14g Romex (parallel, not twisted pair) and connected the devices. I got called when it didn't work. After changing the wiring on one end so Tx was connected to Rx instead of Tx, the link came alive at 4800 baud, if I remember correctly. I was astounded it worked -non-twisted pair, no shielding, longer than the max-spec. That was turn-of-the-century era and it's still running today.
The other situation involved a long weekend (3 day) community fair at the local park that needed a single point internet connection in the early 10Mb internet days, before WiFi was a gleam in anyone's eye, sometime in the late 1990's/early 2000's(?)
The intended service was to update the community's new web site with a web cam photo once a minute to showcase the fair. The nearest household with a "broadband" internet connection (that they could 'borrow') was through the woods on the backside of the park. The organizing committee paid for a big spool of CAT5 and had a couple of teenagers run it through the woods, loosely stapling the cable to a tree every so often. My recollection is that it was about a 1,500 ft (500m give or take) run. The link worked great for that level of service. The committee sent emails, got their once-a-minute web cam updates where attendees oohed and aahed that they could see nearly instant cam updates "over-the-internet".
My recollection is that IEEE's Ethernet spec is 100m. But light duty service will work at longer distances.
At lower baud rates, you might well push RS-485 longer distances than 1200m.
I suspect the distance limitation is the rounding effect capacitance has on the leading edge of a bit. Lower baud rates extend the mid-bit UART "read" so are lower baud rates are more "tolerant" of capacitive distortion.