Modbus RTU to Modbus TCP conversion
K
Kelly
Hi
We developed a device which communicates via RS 232 port using Modbus RTU format. We would like this device to be connected to the ethernet, so that it could communicate with OPC servers that support Modbus TCP format. What is the easiest way to do this?
Is it possible to get some RS-232 to Ethernet converter available out in the market to do the job? If so, are there any recommendation? I would appreciate any comments or suggestions regarding this. Thanks in advance for the help!
Kelly
Benoit Galarneau
Look for Schneider TCP-IP bridge 174-CEV-300-20. They're easy to configure & use, and well documented.
F
Fernando Capelari
There any many Modbus TCP to Modbus RTU converters available in the market, from different vendors. I've personally used the one from Schneider Electric, which part number is 174CEV30020.
You should be able to find its catalog and manual at wwww.modicon.com and then request a quotation at the Schneider Electric office or distributor nearest to you.
Andy Burgess
Schneider have a Modbus to Ethernet bridge. Part number is 174CEV30010. Search on their website for the user manual. It simply converts Modbus RTU/ASCII to Modbus TCP, it is not an OPC server. Cost is just under 500 GBP.
Andy
[email protected]
T
Hello Kelly.
I think there are a few brands of Modbus/RTU to Modbus/TCP gateways on the market. My company, HMS Industrial Networks, is one manufacturer. It is a "transparent" gateway, so it automatically routes Modbus messages between Modbus/RTU and Modbus/TCP. The only programming that you have to do is to set the IP address and the serial parameters for the RS-232 port. You can read about this at our web site:
http://www.anybus.com/products/abxtcp_rtu.shtml
If you have technical questions, feel free to call us at 773-404-3486 and press 5 for technical sales.
Best regards,
Trevor Lang
Suprise, suprise! Schneider Electric makes just such a device. CEV 300 20 converts Modbus TCP-IP to Modbus and visa-versa. Contact a local distributor or one of the many web sites, such as http://www.schneiderelectric.com and search the product. Stuck? Contact me via this site. Many users without issue.
G
Gopesh Sanghvi
Hi Kelly,
The easiest way is to get the some RS-232 to Ethernet convertor.
I have tried Moxa's DE-211 convertor. It works fine.
-Gopesh
Like Brian said you can go with the CEV 300 20 bridge but you can probably get the same product from a third party for half the cost. Also, remember that SE requires a contract for all level 2 technical support.
Jaroslaw Berezowski
They manufacture Modbus TCP-to-serial gateway NPort 6110 - I think the cheapest device available worldwide.
G Modbus 3
P Modbus 15
M Modbus 8
M Modbus 21
L Modbus 2