1. Tell me one thing, i have heard that power system frequency is unified and same everywhere. but is it really the same at the terminals of all generators output when we consider them present in a single area? Suppose my area consists of one hydro and 3 steam units, will the energy be sensed same everywhere at a particular time of load pick up?
Also,i know areas are determined by coherent behavoiur of its residing units, i.e., the units behave similarly to a step load. in that respect would it be practical to consider the hydro unit as one area and the 3 steam units on separate area?
2.Dynamic response is the period (30-40 seconds) when governor acts after the inertial response (2-10 secs phase determined by rotating masses kinetic energy + frequency sensitive loads damping coefficient).
You are telling that speed setpoint of all droop governors are to be changed after the end of this dynamic response period. but i wonder whether the isochronous unit has already brought back the frequency to its setpoint ->50 Hz fully, within the end of this dynamic response period?
Now, I STATE MY DIFFERENT UNDERSTANDING ON TWO SEPARATE PARAS .PLZ LOOK AT THEM INDEPENDANT OF THE OTHER ONE 2A AND 2B.
2a. IF SO, i.e., the iso already does its job at the end of dynamic response phase, the droop units will see that frequency returns to its old value. and therefore it will fully release whatever load it has previously taken out of frequency deviation at the end of this dynamic period, as the frequency deviation due to iso unit is now zero. Now the steady state mode begins and now operator changes droop setpoints either manually or as per some auto load control program so that the droop units can again increase their generation (it has previously increased). and thus relieve the iso unit, which now again decrease its load to offset over frequency on account of change in droop setpoints.
Is that how our power system operates? here the droop units are increasing generation due to sensing negative speed deviation. then decreasing generation due to zero speed deviation, and then again increasing generation as the speed setpoint increase (so again a negative error). So the droop units are doing the same job for twice-thrice the time.
Won't it be easier if we control droop units' speed setpoints automatically within the dynamic response period (assuming the ramping rates of droop units are comparable) before the iso units finish its job of regulating frequency? so that the iso unit on account of its quick (P+I) action gives a much larger share to the step load increase, but simultaneously the droop units also gives a lesser share to this load relatively slow as compared to iso unit.
2b. If NOT SO, i.e., THE ISO UNIT DOESN'T FULLY REGULATE THE FREQUENCY AT THE END OF THIS DYNAMIC RESPONSE. so its integral control is still not finished acting. so now still some frequency deviation remains. and the droop units hold on to its last increased value during dynamic primary governor response and ryt at this moment, the speed setpoint of droop units are changed. So beginning from this moment the iso and droop units are again parallelly acting to regulate the already improved but slightly deviated frequency, back to its scheduled 50 HZ value. and after the order of 2-3 minutes (depending on the step load increase), the frequency returns back to 50hz. and we conclude that droop control + their setpoint changing in one hand and an isochronous unit on the other hand does the same job. but while iso unit is faster (large integral gain), it takes a larger share of step load, and since the integral gain associated with auto setpoint control of droop units is lesser or it is manual change, they take lesser percentage of the step load.
NOw tell me which according to my above two paras 2A and 2B actually goes on the power system w.r.t a step load increase?
Lastly,
>This is different from a system where the dynamic response of a >number of sets is controlled by a single controller, trying ..disturbances.
How this 'number of sets' is decided? Is it by checking the frequency responses? i,e droop coefficients and ramping rates of those 'no. of sets'? or by some other economical consideration? If droop speed setpoint changing, is all about load scheduling and not dynamic response? the i guess the single AGC controller does some kind of droop coefficient control (R control) of the droop units and does not affect the iso unit in any way. Is that it?
Also,i know areas are determined by coherent behavoiur of its residing units, i.e., the units behave similarly to a step load. in that respect would it be practical to consider the hydro unit as one area and the 3 steam units on separate area?
2.Dynamic response is the period (30-40 seconds) when governor acts after the inertial response (2-10 secs phase determined by rotating masses kinetic energy + frequency sensitive loads damping coefficient).
You are telling that speed setpoint of all droop governors are to be changed after the end of this dynamic response period. but i wonder whether the isochronous unit has already brought back the frequency to its setpoint ->50 Hz fully, within the end of this dynamic response period?
Now, I STATE MY DIFFERENT UNDERSTANDING ON TWO SEPARATE PARAS .PLZ LOOK AT THEM INDEPENDANT OF THE OTHER ONE 2A AND 2B.
2a. IF SO, i.e., the iso already does its job at the end of dynamic response phase, the droop units will see that frequency returns to its old value. and therefore it will fully release whatever load it has previously taken out of frequency deviation at the end of this dynamic period, as the frequency deviation due to iso unit is now zero. Now the steady state mode begins and now operator changes droop setpoints either manually or as per some auto load control program so that the droop units can again increase their generation (it has previously increased). and thus relieve the iso unit, which now again decrease its load to offset over frequency on account of change in droop setpoints.
Is that how our power system operates? here the droop units are increasing generation due to sensing negative speed deviation. then decreasing generation due to zero speed deviation, and then again increasing generation as the speed setpoint increase (so again a negative error). So the droop units are doing the same job for twice-thrice the time.
Won't it be easier if we control droop units' speed setpoints automatically within the dynamic response period (assuming the ramping rates of droop units are comparable) before the iso units finish its job of regulating frequency? so that the iso unit on account of its quick (P+I) action gives a much larger share to the step load increase, but simultaneously the droop units also gives a lesser share to this load relatively slow as compared to iso unit.
2b. If NOT SO, i.e., THE ISO UNIT DOESN'T FULLY REGULATE THE FREQUENCY AT THE END OF THIS DYNAMIC RESPONSE. so its integral control is still not finished acting. so now still some frequency deviation remains. and the droop units hold on to its last increased value during dynamic primary governor response and ryt at this moment, the speed setpoint of droop units are changed. So beginning from this moment the iso and droop units are again parallelly acting to regulate the already improved but slightly deviated frequency, back to its scheduled 50 HZ value. and after the order of 2-3 minutes (depending on the step load increase), the frequency returns back to 50hz. and we conclude that droop control + their setpoint changing in one hand and an isochronous unit on the other hand does the same job. but while iso unit is faster (large integral gain), it takes a larger share of step load, and since the integral gain associated with auto setpoint control of droop units is lesser or it is manual change, they take lesser percentage of the step load.
NOw tell me which according to my above two paras 2A and 2B actually goes on the power system w.r.t a step load increase?
Lastly,
>This is different from a system where the dynamic response of a >number of sets is controlled by a single controller, trying ..disturbances.
How this 'number of sets' is decided? Is it by checking the frequency responses? i,e droop coefficients and ramping rates of those 'no. of sets'? or by some other economical consideration? If droop speed setpoint changing, is all about load scheduling and not dynamic response? the i guess the single AGC controller does some kind of droop coefficient control (R control) of the droop units and does not affect the iso unit in any way. Is that it?