Dear sir,
ours is a GE Fr5 - Mk6 speedtronic dual fuel system. Recently when the turbine was running at 8MW load on fuel gas mode and operator tried to change over the operation from fuel gas TO distillate fuel mode, the turbine load swing down below 1.5 MW and breaker opened on reverse power with turbine still running at FSNL. On checking the control system, slot5 VSVO had the following diagnostic alarms in all the 3 core R-S-T.and not getting RESET.
1. Servo current#2 disagree with reference suicide
2. servo current#1 disagree with reference suicide.
3. LVDT#4 RMS volt out of limits.
Under this situation, do I need to "disable" the suicide condition first and then proceed further to find the fault. Pls let me know the trouble shooting procedure. Thanx in advance...
ours is a GE Fr5 - Mk6 speedtronic dual fuel system. Recently when the turbine was running at 8MW load on fuel gas mode and operator tried to change over the operation from fuel gas TO distillate fuel mode, the turbine load swing down below 1.5 MW and breaker opened on reverse power with turbine still running at FSNL. On checking the control system, slot5 VSVO had the following diagnostic alarms in all the 3 core R-S-T.and not getting RESET.