Hi all
My name is Tim vo
We have a GE mark V steam turbine system that control the hydraulic of ETD1 and ETD 2 is trip due to the header pressure from the pressure switch ps282 is zero psi. This is the HPM-15 module for the lube oil skid. Testing the solenoid from external power is working fine. But when running is not. We troubleshoot the GE MARK V and found out that the PTBA CARD pin 59 and pin 60 for etd 1 and pin 63 and pin 64 for edt 2 had low voltage on the positive side instead od 65 vdc but it only read 14 vdc. The negative side is good -67 volts. When we disconnected the load it is back to 65 volts on both positive and negative. Something is pulled down the positive side
Repacing the TCTS CARD and also the PTBA CARD is still the same.
Any suggestions please help
Thanks very much
Tim
My name is Tim vo
We have a GE mark V steam turbine system that control the hydraulic of ETD1 and ETD 2 is trip due to the header pressure from the pressure switch ps282 is zero psi. This is the HPM-15 module for the lube oil skid. Testing the solenoid from external power is working fine. But when running is not. We troubleshoot the GE MARK V and found out that the PTBA CARD pin 59 and pin 60 for etd 1 and pin 63 and pin 64 for edt 2 had low voltage on the positive side instead od 65 vdc but it only read 14 vdc. The negative side is good -67 volts. When we disconnected the load it is back to 65 volts on both positive and negative. Something is pulled down the positive side
Repacing the TCTS CARD and also the PTBA CARD is still the same.
Any suggestions please help
Thanks very much
Tim