I would like to have more details on how the load control reference and IPC control reference is calculated in Mark V for ST application. As I understand, IPC mode is selected to enable the turbine to follow the boilers (V1 to control the inlet pressure with bypass valves remained fully closed) while the load control is selected to enable the boilers to follow the turbine (bypass valve modulated by DCS to control the inlet pressure with V1 remains fully opened).
The reason behind this question is that usually my ST will be put into IPC mode after 30MW following a turbine reset. However after a recent startup, the turbine did not go into IPC mode as the TPWR is lower than IPC in the min value gate. The current setting for IPC was 104% with the TPWR being a calculated figure at about 103.94(TN_LD is set at 104% as well).
What I did to resolve the matter is I increased the TN_LD at HMI from 104% to 105% so that the IPC could be within the control range. I got this idea from GEK 104040 where it was stated that the "LOAD SETPOINT must be manually moved to a maximum after enabling IPC so that IPC can respond to the full range of the inlet pressure demand (if the control system does not move it automatically)"
I would like to know what might be the reason behind this scenario as usually this manual shifting of load setpoint is not done and the unit could be loaded to IPC mode without any problems.
Thanks
The reason behind this question is that usually my ST will be put into IPC mode after 30MW following a turbine reset. However after a recent startup, the turbine did not go into IPC mode as the TPWR is lower than IPC in the min value gate. The current setting for IPC was 104% with the TPWR being a calculated figure at about 103.94(TN_LD is set at 104% as well).
What I did to resolve the matter is I increased the TN_LD at HMI from 104% to 105% so that the IPC could be within the control range. I got this idea from GEK 104040 where it was stated that the "LOAD SETPOINT must be manually moved to a maximum after enabling IPC so that IPC can respond to the full range of the inlet pressure demand (if the control system does not move it automatically)"
I would like to know what might be the reason behind this scenario as usually this manual shifting of load setpoint is not done and the unit could be loaded to IPC mode without any problems.
Thanks