I have. ^^! It's quite good so that to follow and review the engine speed.Use Chart recorder too it help for PID tuning ....
I still do not know if the problem is related top Diesel engine (Prime mover ) than Generator itself...The main problems is how to control the generator with sudden load test
Derivative gain is decreased from 25 to 12...can you expalin why ...Thank you @ControlsGuy25
I used PST to record RPM when I increase load and then load steady to check when there is abnormality.
I adjust the parameter by User interface because the generator reacts faster than adjusted with PST.
Attached photo below is a original of the generator. And it's not control the generator when the load increase from 0 to 50% load and decrease from 100% to no load.
I will increase the P ( Proportional ) and D ( Derivative ) and OVG to control the generator.
I will continue to check next Monday. If It will be OKE, I will begin the synchronizing 2 generator. The generator use AVR MX341 board.
Looking forward to your support ? Thanks
It's from the manufacturer and that also is my question ^^! I think it is the best choice from them.Derivative gain is decreased from 25 to 12...can you expalin why ...
Hi james,I still do not know if the problem is related top Diesel engine (Prime mover ) than Generator itself...
What you mean by "control the generator " ...you should provide details on droop /isochronous mode scheme installed..
Regarding the datas that you provided ...and assuming that tehre is no alrms coming from AVR ..problem reside mostly on Prime mover controls system configuration /tuning...
Cheers.
James
Hihi lee tons same problem now I'm facing.
kindly assist me to solve the same problem. I'm adjust PID value but problem still present.
| Thread starter | Similar threads | Forum | Replies | Date |
| İ | İnvt modbus rtu start stop problem | Modbus | 5 | |
| R | Mark VIe - E-Stop 1 Protective Circuit Latched | Power Generation | 1 | |
| A | Mbus water meter stop talk after some hours | General Communications Chat | 11 | |
| M | Emergency Stop Machine Interconnection | General Automation Chat | 9 | |
| B | E-Stop circuits in machine tools | General Automation Chat | 20 |