We are experiencing strange behavior reading the 4-20mA signal from a pressure transducer on a water storage tank.
We are reading the 4-20mA signal into a 0-10V analog input on an AB MicroLogix 1100 using a resistor (initially 500ohms) across the input. The system is being powered by a 12VDC battery and associated charger.
Initially we used an existing transducer that is rated to operate on 10-36VDC power. Measured voltage powering the sensor was 13.2VDC. We found that this sensor was not capable of driving the output to 10V at 20mA, but appeared to be able to drive 5V across a 250ohm load at 20mA. During testing we would bleed the pressure from the sensor to read zero and then restore the pressure to around 42 psi(15mA). If we restored the pressure too rapidly, the sensor would "saturate" and give us approximately 20mA signal and would not drop back to 15mA after the pressure would equalize.
Only by momentarily shorting across the 250mA load would the signal clear and return to expected readings.
After "resetting" the signal we left the system only to find a short time later that the signal had once again saturated.
A new sensor from a different manufacturer was purchased in an attempt to address this problem. We found similar behavior from the new sensor. The manufacturer confirmed the need to "reset" the sensor after reaching a saturated state. After placing into service this sensor successfully read the tank level down to 14mA region but then "stuck" at that reading, even after the tank was refilled to a higher level.
We have installed dozens of similar systems without ever experiencing this phenomenon. The only difference is that the other systems drove the sensor at 24VDC instead of 12VDC.
Is anyone familiar with this phenomenon and can explain how to address it?
Thanks!
Ron Davis
We are reading the 4-20mA signal into a 0-10V analog input on an AB MicroLogix 1100 using a resistor (initially 500ohms) across the input. The system is being powered by a 12VDC battery and associated charger.
Initially we used an existing transducer that is rated to operate on 10-36VDC power. Measured voltage powering the sensor was 13.2VDC. We found that this sensor was not capable of driving the output to 10V at 20mA, but appeared to be able to drive 5V across a 250ohm load at 20mA. During testing we would bleed the pressure from the sensor to read zero and then restore the pressure to around 42 psi(15mA). If we restored the pressure too rapidly, the sensor would "saturate" and give us approximately 20mA signal and would not drop back to 15mA after the pressure would equalize.
Only by momentarily shorting across the 250mA load would the signal clear and return to expected readings.
After "resetting" the signal we left the system only to find a short time later that the signal had once again saturated.
A new sensor from a different manufacturer was purchased in an attempt to address this problem. We found similar behavior from the new sensor. The manufacturer confirmed the need to "reset" the sensor after reaching a saturated state. After placing into service this sensor successfully read the tank level down to 14mA region but then "stuck" at that reading, even after the tank was refilled to a higher level.
We have installed dozens of similar systems without ever experiencing this phenomenon. The only difference is that the other systems drove the sensor at 24VDC instead of 12VDC.
Is anyone familiar with this phenomenon and can explain how to address it?
Thanks!