Hai Guys,
Presently I have problem with VCMI & UCVH card on R core, which is failed to communicate via ToolboxST. Before rebooting the R rack, VCMI still communicate with others I/O modules & no IONET issues, only the UCVH failed to communicate with ToolboxST (message: Error connecting to target: 192.168.XXX.XXX windows socket operation failed). However, after power cycle (Reboot) on R rack the VCMI failed communicate to the I/O modules and UCVH shown red led lit at all.
Action has been taken:-
1). Power off R rack and pull out UCVH for Re-flash CF memory.
2). Download Compact Flash for R & successful. Insert the CF memory in UCVH. Installed UCVH into R rack and power up.
3). Ping the IP address & successful replied. Then download pcode runtime & application code, to permanent storage only.
4). Power down the R rack for 3 minutes and power up again. The UCVH red led still lit and failed to communicate.
5). Now I replace the VCMI card with new spare by follow the instructions as stated in GEH-6421. However, after power up the R rack, the problem still exist.
Appreciate if you can provide any advice. Let me know if you need more information.
Thanks
Presently I have problem with VCMI & UCVH card on R core, which is failed to communicate via ToolboxST. Before rebooting the R rack, VCMI still communicate with others I/O modules & no IONET issues, only the UCVH failed to communicate with ToolboxST (message: Error connecting to target: 192.168.XXX.XXX windows socket operation failed). However, after power cycle (Reboot) on R rack the VCMI failed communicate to the I/O modules and UCVH shown red led lit at all.
Action has been taken:-
1). Power off R rack and pull out UCVH for Re-flash CF memory.
2). Download Compact Flash for R & successful. Insert the CF memory in UCVH. Installed UCVH into R rack and power up.
3). Ping the IP address & successful replied. Then download pcode runtime & application code, to permanent storage only.
4). Power down the R rack for 3 minutes and power up again. The UCVH red led still lit and failed to communicate.
5). Now I replace the VCMI card with new spare by follow the instructions as stated in GEH-6421. However, after power up the R rack, the problem still exist.
Appreciate if you can provide any advice. Let me know if you need more information.
Thanks
Attachments
-
68.8 KB Views: 13