Sear CSAoussama el,
I want to add: Normally, when GE (USA) provides a 125 VDC battery and charger for a Mark* turbine control there is no ground (earth) detection card in or earth condition detected by the battery charger. Earth detection is performed by the Mark*. Many times, unfortunately, when a Customer with a Mark* buys a new battery charger they mistakenly buy one with earth detection capability--and if the earth detection in the Mark* is not blocked the earth detection of both systems are adversely affected (the business of resistors in parallel reducing the resistance to less than the lowest resistor value). This can cause erroneous earth indications in BOTH the battery charger AND the Mark*. AND it can make locating Earth's very difficult.
It's also VERY IMPORTANT to understand that the earth detection of the Mark* and the battery charger CANNOT distinguish between Earth's in devices connected to the Mark* and other devices powered by the battery--contrsry to false and extremely popular belief. ANY EARTH ON AMY DEVICE OR CIRCUIT CONNECTED OR POWERED BY THE 125 VDC BATTERY IS REPORTED AS AN EARTH BY THE MARK* OR THE BATTERY CHARGER!!! That's right--an earth in the DC Hydraulic Ratchet Pump motor field circuit will be detected by either system as an earth EVEN THOUGH the DC Hydraulic Ratchet Pump motor field circuit is not connected to the Mark*. Same for an earth in the DC Emergency Compartment Lighting circuits. The Mark* ESPECIALLY cannot separate devices powered directly by the 125 VDC battery that are connected to the Mark* from devices which are also powered by the 125 VDC battery but NOT connected directly to the Mark*--again, contrary to false and popular belief. The Mark* just CANNOT distinguish between devices connected to the Mark* and devices not connected to the Mark*.
So, if the earth detection hardware jumper is IN in the <PD> core AND there is an earth detection card or function operating in the 125 VDC battery charger, the two are working"against" each other and they should not both be active or enabled simultaneously. And if they both are then detecting earths is going to be difficult and time-consuming. But, in reality neither will properly detecting an earth if both are enabled at the same time.
Again, if the same thing is happening to two or more units then it's very probable two (2) Mark VI turbine control panels have NOT failed in a similar manner and at nearly the same time. It's more likely that something similar or shared by the two Mark* turbine control panels is/are failing or failed. That could be ANY NUMBER of things, from earthing systems to temperature/humidity control (or lack thereof), or housekeeping (dust and dirt), to <DACA> power supplies, to dirty 125 VDC battery charger output(s), to failing/failed rack-mounted power supplies, to VPRO power supplies to earths. And, it could also be a combination of any (or all) of the above. Failure to adhere to industry standard earthing protection schemes and regularly testing and properly maintaining earthing systems can also contribute to or be the entire problem. Someone connecting a 440 VAC motor to the Functional earthing system, or connecting a field device to the Protective earth system. Or a shield drain wire to the Protective earth system--all of these could compromise the integrity of the independent earths. A change in the moisture content of the soil the earths are buried in, or a separation of earthing components in a particular system could also contribute to or be the problem.
Look for something similar to both machines or common to both machines as the root cause of the problem; that could ultimately lead to a failure of Mark* components or cards--but simply replacing the failed Mark VI card or component IS NOT resolving the root cause(s) of the problem and will only lead to more failures.
Again, please write back to let us know how the problem resolution is progressing!
Thanks for your reply status of plant now we decided to switch of 125VDC from battery charger for each unit.
Each unit has separate 125VDC . and so far units stable and no trip. we will monitor the units and update you for any news.
can you please tell me the reasons make VCMI card reboot ?
Thanks and best regards