we are having an issue with a GT13E2 unit (VGIV Measurement Difference Alarm), and its recurring with no trace of what is triggering the signal.
we did following activities as recommended by OEM:
however the issue still persist, data and trends shows that it happnened on load 70 MW and 35MW but we are not sure if there is a link between low load and the issue because we still don't know what is the root cause of the alarm.
i hope that someone in this forum has ever faced this issue before.
we did following activities as recommended by OEM:
- Remove the connection between shield and ground from VIGV transmitter side.
- Add a capacitor between the shield and ground in the JB for VIGV transmitters.
- Check the ground point connection in the Marshaling for VIGV transmitters.
- Check the calibration for VIGV transmitters
- Reduce the low pass filter in ControCad from 50 to 10
however the issue still persist, data and trends shows that it happnened on load 70 MW and 35MW but we are not sure if there is a link between low load and the issue because we still don't know what is the root cause of the alarm.
i hope that someone in this forum has ever faced this issue before.