This is for gas turbine vibration protection
vibration limit 12.5mm /s for Alarm
and 25mm/s for trip is taken
whether these values relate to RMS or 0-peak or peak to peak if you get voltage from velocity transducer.
it generates 150 mv/ips from Metrix transducer in RMS but if system demand 1 inch/s peak to peak.
then the voltage input should also be 150 mv pk-pk which is only 53 mv RMS or 100 mv 0-pk
what is the correct limit to be taken for protection of the machine because this will change the whole parameters 1/3 times or 2/3 times than the RMS values?
will any body clear the whole calculation for gas turbine frame 6?