On 30th June 2024, unit was running on part load. Below diagnostic alarms occurred followed by all Turbine Radial and Thrust Bearing temperature TX became bad i.e. the signal quality turned bad state. Below is the alarm Log extracted from MARKVI:

It is quite evident from the first diagnostic alarm “Pack internal reference voltage out of limit” i.e. there was some issue in the supply of card. Anyhow, INST cut off the communication and replaced the faulty card. The bad signals became healthy after card replacement.
Instability in the power supply can cause the internal reference voltage to fluctuate. Trends of UPS system as well as DC system checked/analyzed, but no significant change observed.
Previously we have faced similar events of Card failure. Anyone can suggest the failure root cause of these cards in MARKVIE?
Thanks in advance.
Regards
Muhammad Bilal

It is quite evident from the first diagnostic alarm “Pack internal reference voltage out of limit” i.e. there was some issue in the supply of card. Anyhow, INST cut off the communication and replaced the faulty card. The bad signals became healthy after card replacement.
Instability in the power supply can cause the internal reference voltage to fluctuate. Trends of UPS system as well as DC system checked/analyzed, but no significant change observed.
Previously we have faced similar events of Card failure. Anyone can suggest the failure root cause of these cards in MARKVIE?
Thanks in advance.
Regards
Muhammad Bilal