what can be causing a flame detector for frame 6B gas turbine to failing constantly.

what can be causing a flame detector for frame 6B gas turbine to failing constantly.
thanks for your usual cooperation
What kind of unit controls systems ??

What are the alarms taht have been annuciated ??

There could be differents reasons, why flame detector/scanner/trakker fail I had troubelshoot some units, with condesing lens issue corrected with an with upgrade/modification on devices/parts and flexibles.

We can try to support you with valuable datas that you can provide

Hope this can be an higlighting!
ControlsGuy25.
 
Thanks
the alarm annuciated is that: flame detector trouble on the HMI screen so after that the flame detector was replace with another one.
unit control system is speedtronic mack VI frame 6B
 
Thanks
the alarm annuciated is that: flame detector trouble on the HMI screen so after that the flame detector was replace with another one.
unit control system is speedtronic mack VI frame 6B
Akin,

Can you precise Type/OEM of the flame detector ??

What the flame intensity is whith the old and new falme scanner/detector???

How the Devices are mounted in your turbine compartment ??

Is there cooling water system equipped??

Controls Guy25.
 
Top