Is it possible to program Modbus-port #2 of Quantum 140CPU43412A CPU module with XXMIT function block?

And is it possible to use Modbus-port #2 of Quantum 140CPU43412A CPU module as Modbus Master?

Thanks for your support.
 
R

Rafael N. Jacomino

No, the Quantum PLC cannot employ Port #2 through the XMIT/XXMIT instruction. Only on the Momentum, you can use both ports for XMIT/XXMIT communication. Port #2 on the Quantum works strictly as a ModBus slave. However, the cost of the Momentum is so low (and it already includes the XMIT/XXMIIT loadable), you might want to Peer-cop with it from the Quantum ModBus Plus port. Creating sort-of a simple and fast "intelligent gateway." Good luck.
 