I have been asked to look at the blackout of a refinery. It happened during a grid collapse when the frequency dropped to zero. Before the refinery could go into island mode, one of its main GE gas turbines tripped on High Exhaust temperature. It was operating in droop mode. It would have been taking full load from 49.4 Hz (50Hz system) and tripped circa 48-48.5Hz approx 3 seconds after moving to full load.
Question: Why could the MkVI not control the load on the machine / to avoid the high exhaust temp trip and just maintain full load output ?
Its a Frame 6 Nominally rated 47MW. Prior to the event it was loaded 39MW, with 19MW being exported to the grid.
Any pointers / advice ? Could this trip have been avoided ?
and
The islanding action was initiated at 47.5Hz. This was set because of grid compliance for power generators which may be less appropriate for a refinery that has a dual function to provide power to the grid from its cogen plant but also a responsibility to continue to operate its own process and successfully survive a collapsing grid frequency (it has enough own generation and load shedding).
Has anyone got knowledge of examples where a utility has accepted higher setting from a refinery/power generator for the underfrequency trip ?
Cheers,
Paul
Question: Why could the MkVI not control the load on the machine / to avoid the high exhaust temp trip and just maintain full load output ?
Its a Frame 6 Nominally rated 47MW. Prior to the event it was loaded 39MW, with 19MW being exported to the grid.
Any pointers / advice ? Could this trip have been avoided ?
and
The islanding action was initiated at 47.5Hz. This was set because of grid compliance for power generators which may be less appropriate for a refinery that has a dual function to provide power to the grid from its cogen plant but also a responsibility to continue to operate its own process and successfully survive a collapsing grid frequency (it has enough own generation and load shedding).
Has anyone got knowledge of examples where a utility has accepted higher setting from a refinery/power generator for the underfrequency trip ?
Cheers,
Paul