I have following questions regarding a base load nuclear power plant connected to an infinite grid:
1)Assuming plant control systems are too slow to respond to load rejection transients. In case of partial load rejection how is it possible for the plant turbine speed to overshoot and lose synchronisation with the grid resulting in disconnection? Because even if plant does not decrease its power quickly it should remain connected and keep pumping excess amps forcing other connected load following plants to reduce their power. Can we say that a plant connected to an infinite grid that does not respond quickly enough to load rejection transients due to slower response time or faulty controls should not disconnect from grid unless grid frequency crosses limits?
2) Assuming following characteristics:
Plant can reject or increase load at 5%F.P./Min ramp and 10% F.P. Step load without opening of steam dump valves. Since the plant is base load and operates at full power therefore, in case of decrease in grid frequency it is impossible for this plant to increase its power. For load rejections, how plant droop should be set? Equal to overall droop setting 5% or 4% or at some higher value because its a base load plant and it should not respond to fast changes in load rejections? Should there be any droop settings at all?
1)Assuming plant control systems are too slow to respond to load rejection transients. In case of partial load rejection how is it possible for the plant turbine speed to overshoot and lose synchronisation with the grid resulting in disconnection? Because even if plant does not decrease its power quickly it should remain connected and keep pumping excess amps forcing other connected load following plants to reduce their power. Can we say that a plant connected to an infinite grid that does not respond quickly enough to load rejection transients due to slower response time or faulty controls should not disconnect from grid unless grid frequency crosses limits?
2) Assuming following characteristics:
Plant can reject or increase load at 5%F.P./Min ramp and 10% F.P. Step load without opening of steam dump valves. Since the plant is base load and operates at full power therefore, in case of decrease in grid frequency it is impossible for this plant to increase its power. For load rejections, how plant droop should be set? Equal to overall droop setting 5% or 4% or at some higher value because its a base load plant and it should not respond to fast changes in load rejections? Should there be any droop settings at all?