The sites are old, GE doesn't support anymore - and with the state of GE today, it seems hard to find good motivated help to dig into anything. These are purchased units and we can't find complete manuals including control spec - I have one from the units WITH the logic. Those units do have IBH - they units with allowed continued operation with CBVs open do NOT. I agree with you on the risks for combustion operation - BUT the site (allowed to run) argues: transfers from primary to lean-lean to secondary transfer to Premix baseload ops is smooth. Good point on primary zone reignition - instead of absolutely trusting the site is correct, I'll hunt through PI and validate with flame eyes indication and exhaust T/Cs.Interesting dilemma--the difference in logic. It would be very interesting to understand why, from the OEM. Have you tried looking at the Control Specification drawings for the various sites to see if they have any "information"?
| Thread starter | Similar threads | Forum | Replies | Date |
Gas turbine compressor bleed valve fail to close | Power Generation | 2 | |
| D | Limit Switches on Compressor Bleed Valve | Power Generation | 18 | |
| B | Compressor Bleed Valve Failure: Causes and Recommendation | Power Generation | 3 | |
| A | Compressor Bleed Valve Position Trouble | Power Generation | 3 | |
| R | Compressor bleed valve problems | Power Generation | 5 |