We use Condensing pots to measure steam flow. Recently we noticed a decrease in the steam flow. Based on the thermography, we found high side condensing pots at ambient temperature while the low side condensing pot was at steam temperature (400 deg F).
We suspect non-condensables in the low side. We normally do not Vent the condensing pots but after this issue, we vented the condensing pots. After the venting, no change in the flow was noticed but both Condensing pots were measured at steam temperature (400 deg F). Within a week, the high side condensing pot again returned to ambient temperature (105 deg F). We are not sure if there is any water in the water leg and how to check it. Any help will be greatly appreciated. Also, if there is any literature that I can look at to get better understanding.
General description of the setup is: Two taps on the steam line. One upsteam of the flow orifice and one downstream of the flow orifice. Both taps go to the vertically mounted Condensate Pots. The drain at the bottom for both pots go to the transmitter.
[email protected]
We suspect non-condensables in the low side. We normally do not Vent the condensing pots but after this issue, we vented the condensing pots. After the venting, no change in the flow was noticed but both Condensing pots were measured at steam temperature (400 deg F). Within a week, the high side condensing pot again returned to ambient temperature (105 deg F). We are not sure if there is any water in the water leg and how to check it. Any help will be greatly appreciated. Also, if there is any literature that I can look at to get better understanding.
General description of the setup is: Two taps on the steam line. One upsteam of the flow orifice and one downstream of the flow orifice. Both taps go to the vertically mounted Condensate Pots. The drain at the bottom for both pots go to the transmitter.
[email protected]